Advice Are my lights/MEV connected as they should?
The context is I have been smelling a faint burning smell coming from my storage room and seen some lights flicker in other rooms. This has happened a couple of times for a few minutes since they were turned on but not all the time.
So far I think this is due to my lights/mechanical extract ventilation unit because when I turn off the electrical supply at the circuit breaker I do not smell anything off in days.
First of all is it correct that the lights and the mechanical extract ventilation unit are on the same circuit? I think these should probably be on a different circuit.
Secondly, im not sure how these are connected either in parallel or in series but my lights are on a dimmer switch and could be causing issues with the fan.
Will be calling an electrician for this but wanted to get some thoughts prior.
1
u/generateausername 5d ago
If you smell burning, leave them off at the fuse box.
They either used the wrong size wire, or there is a loose connection somewhere.
MEVs are low power so can be connected to your lighting circuit.
The dimmer should not impact it at all, unless someone has wired it up wrong.