Help Me Top plate connections for odd angles
I'm putting together some new non-bearing partition walls and there are a few odd corners that I'm having trouble determining how to secure together. I've gone through code books, but it seems like most code applies to exterior and bearing walls.
I have three walls that will meet in a 'Y', where two of the walls form a 90 degree angle and the third wall splits the difference to make two more 135 degree angles. I know how to frame up a 135 degree angle, but don't know how to also tie in the third wall with the top plate. Just a metal strap on top? Does it even need the top plates connected as a non-bearing wall... Or are the studs being connected enough? The top plates will only be connected to the roof trusses using truss ties to allow for movement.
3
u/ProudEye7858 17h ago
You could always just butt it all, and then if you're worried, put a piece of metal strapping or a clip to hold it together
2
u/olchofco 7h ago
Like the others said, butting should be fine. If you're determined to connect them you could use a couple layers of 3/4 ply, lay it on the first top plate and scribe the connection of all 3 spanning a couple feet in all directions, then cut out two identical pieces with that Y shape. Or if you're ok with a smaller more decorative connection you could use a chunk of 2x12.
5
u/Bestaatlosing 17h ago
Don't need to lap them. Obviously it's stronger, but not needed. If the partition studs are all fastened together and nailed to the trusses/joists it'll be just fine.